07-07-2009 09:33 AM
Hello, I am trying to deploy a program on the real time controller of a compactRIO. I decided to use scan mode for now. However, when I try to run my VI I get the following error:
One or more items in this deployment require the NI Scan Engine and corresponding I/O driver(s) to be installed. Go to MAX to install.
If you continue to encounter this conflict, refer to the "Deploying and Running VIs on an RT Target" topic in the LabVIEW Help for information about resolving target deployment conflicts.
I have LabVIEW real time on my machine so I don't know what the reason for this is and I can not find under MAX where to install the scan engine (again I assume it is already installed).
I am using LabVIEW 8.6.1 and the modules I use on my cRIO-9073 are the 9477 DO module and the 9205 AI module. Any help would be appreciated.
Solved! Go to Solution.
07-07-2009 09:38 AM
Hi Pawel,
you have to install the NI RIO driver on you cRIO (but first in your PC). After that, go to the MAX and select your cRIO. There is a software point. Click on it and install the NI Rio driver on your cRIO. The newest version is 3.1.1.
You'll find it here.
Mike
07-07-2009 09:42 AM
Thanks Mike, that makes sense; I only had 3.0.0 loaded on there. Installing now.
02-24-2014 01:14 AM
if I tried to install the software software at the NI Max
but it give error
"The selected target does not support this function"
how to fix this error,
what problem with it
thank you
Msyafiq
02-24-2014 08:57 AM
It looks like you haven't assigned an IP address to your target. If you don't have a DHCP server running make sure you assign a free IP address that is on the same subnet as you are.
Hope that helps.
02-16-2021 07:11 AM
Hi MikeS81
I have the same problem, I am trying to deploy a program on the real-time controller of a CompactRIO 9024.
I wanted to use scan mode. However, when I try to run my VI I get the following error:
One or more items in this deployment require the NI Scan Engine and corresponding I/O driver(s) to be installed. Go to MAX to install.
If you continue to encounter this conflict, refer to the "Deploying and Running VIs on an RT Target" topic in the LabVIEW Help for information about resolving target deployment conflicts.
I have LabVIEW real-time 2019 on my PC. I am using LabVIEW 2019, NI RIO 19.0 and CompactRIO 19.0 (May 2019) and also it is already installed NI Scan Engine 8.0.
I am using LabVIEW 2019 and CompactRIO 2019 and the modules I use on my cRIO-9024 are the 9425 DI module.
Any help would be appreciated.
Regards,
02-17-2021 03:16 AM
Have you installed the correct drivers on the RIO?
The RIO needs the correct drivers with the versions for LabVIEW 2019 to be able to receive your code.
Also what is your project settings for the RIO. In the project setting for the RIO you can setup the Scan Engine.
02-27-2021 12:11 AM
Yes, I installed the correct drivers on RIO and setup the Scan Engine mode, but It doesn't deploy.
Finally, I figured out the start time of CRIO was in 2060, I sync the time of CRIO, then my project deployed. 👍👍👍👍