07-17-2020 09:10 AM
hello,
I using NI Compact RIO 9073. In that my RT target is not deploying. when it is deploying it shows memory is full.
when i reinstall the software and deployed. my RT target deployed. but its show popup screen has Error 54 occurred at udp open in ****.vi and i verified my udp port and then again i deployed my RT Target it shows memory full.
reinstall the software again its shows same error 54.
Crio 9073
Physical memory is 120 MB
Free Physical memory is 5 MB or 3MB (after reinstall the software)
please hepl me for the solution.
Solved! Go to Solution.
07-17-2020 09:13 AM
Hi Balaji,
the cRIO907x is an old (and deprecated) device, one of its disadvantages is the little RAM available.
To use it you need to strip down the installed software to your minimum requirements.
I was able to use such devices with about 40-60MB free RAM after software installation…
07-18-2020 12:01 AM
Thanks for the reply...
When i install minimum software. my RT target is deployed. but, after deployed popup screen shows Error 54 error occurred in UDP open *****.vi.
so give me solution for this particular error (Error 54 error occurred in UDP open *****.vi)
I tried my UDP communication in another RIO controller. it is communicating with my RT target and PC HMI.
Tell me solution for the er
07-18-2020 02:33 AM