I'm using an SCC-TC02 thermocouple module in the SC-2345 SCC Carrier.  The DAQ card I'm using is the PCI-6221.  I understand that the SCC-TC02 has an onboard thermister for cold-junction compensation.  When setting the parameters for the DAQmx Create Channel.vi, I set the CJC Source to Built In.  By doing so, I assume that nothing else needs to done to compensate for cold-junction (no software conversion, etc.)  I have attached my vi.

 

Thanks in advance.

0 Kudos
Message 1 of 6
(3,440 Views)

Correct.

 

Give it a try and reply back if you have any issues.

Message 2 of 6
(3,411 Views)
I put my therocouple probe in an ice slurry and measured 0.98 degrees C.  I assume that this error was associated with the test set-up since I could watch the temperature gradually increase as the ice melted.  Also, only about half the length of the thermocouple probe was submerged in the slurry.  Any thoughts?
0 Kudos
Message 3 of 6
(3,391 Views)
That sounds pretty good to me.  What is the problem?
0 Kudos
Message 4 of 6
(3,389 Views)
Didn't know how close to 0.0 I should expect my reading to be.  How much would the error be if there was no cold junction compensation in place?
0 Kudos
Message 5 of 6
(3,376 Views)
Solution
Accepted by topic author VI_Joe
Without CJ compensation, the error would be based on what the cold junction temperature is vs. what you typed in as a constant.  So if you said room temperature was a constant 70degF, but it is in realtiy 75degF, then you'll have 5 deg F error in your reading.