9411 Digital Input Issue
I have an issue with a 9411 digital input module. With nothing connected to it I am seeing 1.5V between the digital input and ground. It is causing me to get erratic readings with an encoder. Has anybody else experienced this before?
-Jonathan
(1,480 Views)
-Jonathan
How are you measuring the @1.5V if nothing is connected to it?  Something is obviously connected or there could be no measurement!
"Should be" isn't "Is" -Jay
(1,471 Views)
Flying leads
(1,469 Views)
Hi JWright,
@jwright30 wrote:
Flying leads
Why do you measure voltage on flying leads connected to a digital input?
The more interesting questions:
  • What does the DI module tell you about the state of that DI channel?
  • How much current does the DI deliver on those "flying leads"?
  • Why do you care about unused DI channels?
  • What do you want to coneect to that DI channel?
  • Which of the possible connection types do you intend to use?
(1,451 Views)
I'm measuring the voltage because the digital input signals are showing as on with nothing connected. I was having issues with a single ended encoder and during investigating it I noticed every channel was showing as on, which led me to measure the voltage with a multimeter. I don't know the current it delivers. I'm about to replace the module and see if the problem is still there.
(1,447 Views)
Accepted by IlluminatedG
(1,422 Views)
Fixed the issue with a pull down resistor from the digital input to ground. Thanks for the helpful questions
(1,399 Views)
