Bo,
1a) All FieldPoint I/O modules are supplied operating power from the power supply in the network module. Certain modules may require additional power for sourcing power via outputs or inputs. Of the modules you list above, the following module requires external power; FP-AO-200. The following modules do not require external power wired to the V & C terminals; FP-AI-100, FP-AI-110, FP-TC-120, and FP-RLY-422. The V & C terminals are provided on modules that do not require them to simplify wiring (e.g. not requiring external terminal blocks if you have loop powered current transmitters).
1b) The FP-RLY-422 is rated for up to 3 amps at 35 VDC or 250 VAC. Currents above 3 Amps may damage the relays, the traces on the terminal base and FP-RLY-422 PWBs, and wi
ll cause overheating of the connectoer between the terminal base and the I/O module.
2a) You can use the FP-RLY-422 with a PID control algorithm to control the heater. However, as relays have limited life expectancies and are simply on/off the control will not be a fine as some other options. What may be better is to use a FP-PWM-520 pulse width module to control the solid state relays. You still control the solid state relay via on/off, but in this case, the on/off time can be occuring relatively quickly, and you change the amount of on time vs the amount of off time, to control the power going in to the heater.
Aaron
LabVIEW Champion, CLA, CPI