It is possible that the PID controller has undocumented compensation for lead length and the PID controller also accepts thermocouple and voltage inputs. The PID controller uses constant excitation rather than pulsed.
I have 3rd party software to generate a calibration curve based upon deviation from a reference standard along the operating range. It should be noted that the deviation from reference is NOT linear along a 5 point test from 40° to 120°F. A 2nd order or greater fit is required to match the curve to the FP output. I wouldn't expect lead resistance to have this effect. Could there be an issue with the cable capacitance and the pulsed excitation current?
Unfortunately, my FP modules are temporarily inaccessible, so I cannot conduct tests until next week. The first test will be the same test arrangement with discrete 18 AWG conductors of comparable length. I will also connect a "PID" cable in place of the "FP" cable - this should have no effect, but could rule out the possibility of a spool of defective cable.
Thanks for your help.