FOUNDATION Fieldbus
any experienced Foundation Fieldbus users with ABB CI852
Trying to upgrade a large Foundation Fieldbus installation which uses ABB CI852 communication modules.  Have upgraded f/w on ABB800xA System AC800M Controllers and CI852 modules.  When trying to verify the Foundation Fieldbus I am unable to see the CI852 modules as devices on the bus.
(8,322 Views)
Hi rwbABB,
There are several things that you need to check. Because you have upgraded the firmware of the module (H1 device?), I think the big possiblity here is the restoration of device type, device address, along with some other advanced settings.
Please refer to Appendix B - Missing Device of NI-FBUS Configurator Manual.pdf.
The same file is also available on ni.com here.
(8,297 Views)
LewisL,
Thanks for your response.  I found the issue to actually be with the cable assembly from the PCMCIA card to the bus.  Although I had used the cable on site for testing it was not working once I set up to do my testing off-site.  The connector to the PCMCIA was in quite bad shape to begin with and just never could get it working.  Another cable did the trick.
RWB
(8,274 Views)
