Hello,

 

I am using a CDAQ chassis 9172 with a 9423 module and a 9425 module.

 

Can I make correlated measurements with the 9423 AND static reading with the 9425 at the same time?

 

I am thinking of creating 2 separate tasks for this.  One task for the corellated measurements and one for the static.  Would this work?

 

Thanks

 

Dan

Dan Shangraw, P.E.


   

0 Kudos
Message 1 of 3
(3,629 Views)
Solution
Accepted by topic author ASTDan

Absolutely.  With the cDAQ-9172 you can have 1 correlated digital input task, 1 correlated digital output task, and any number of static digital tasks running at the same time.

 

On the cDAQ-9172 the modules in the correlated digital tasks need to be in slots 1-4.  There is no slot restriction on static digital tasks.

 

Just as heads up, the NI 9425 can currently *only* do static input, but that looks like what you want.

 