Hello Helen,
I made some small modifications to your scheme.
Firstly, you have to connect the "Condition1" block to the systemtact
as well. Otherwise it wont be stopped by the stoptrigger and the whole
scheme can not be terminated with the button.
Secondly, the lamp indicator is a bit trcky to use. This is because it
is not, as you might expect, simply a boolean indicator. Actually it
can display more than 2 states - each state in a different color.
You have to edit the value range for the incoming data and chose which
values are represented in which colors. (Dialog Signaldarstellung ->
Darstellung -> Zustände) in the german version.
Set the indicator to display until 0 in black and until 1 in red and it will work correctly in this case.