i installed fieldpoint 5.01 with labview 7.1 support. but MAX does not detect the field point hardware FP-1000, FP-TC-120 (2 of them). Could you please tell me what is wrong?
Right clicking data neighbourhood and clicking create new does not show me Fieldpoint hardware in the list.
06-18-2007 03:38 PM
Hi Kunal227,
Are you working with this FP-1000 on the same computer, or is this a new computer? Does it detect the FP-1000 and not the FP-TC-120s, or does it not detect anything at all? You can try switching ports if you have more ports available. Also you could try another serial cable, unless you know that one works for sure.
06-18-2007 04:51 PM
i am working on a different pc and it does not have any extra serial ports
MAX does not detect the FP-1000 as well as the FP-TC-120. i have a few other devices attached to the system
one is SCXI daq hardware and a pci-gpib card. but the addresses are different. these devices are detected and working.
i have tried the serial cable on other system and its working.
let me send you a pic of max may be it will give u more idea whats wrong.
06-18-2007 05:22 PM
this is the image i took of the MAX . i don't know how useful it might be.
when i right click the Data Neighbourhood>create new. then it does not show the field point device int he list.
06-19-2007 10:51 AM
Hi Kunal227,
Have you verified that your serial port on that computer works correctly? You can try a loop back test to ensure that it is. The procedure for a loop back test can be found in the second step in this document. If your serial port fails the loop back test, you can get a usb to serial converter to connect your FP-1000 to your computer.
06-19-2007 04:32 PM
it detected finally. i think something went wrong with the cable recently. it was working well before.
anyways thanks for the help.
06-28-2007 12:07 PM
06-28-2007 05:16 PM
06-29-2007 10:27 AM
The default setting is for the [c]FP-TC-120 to enable cold-junction
compensation for all temperature measurements. To disable this
feature and use a software algorithm instead, set the
CJC Sourceattribute of the CJ Temperature channel to either 0 or 25 °C.
Selecting one of these settings causes the [c]FP-TC-120 to assume
a cold-junction temperature of either 0 or 25 °C for all temperature
readings. Regardless of the setting of the CJC Source attribute, CJ
Temperature continues to reflect the actual measured temperature
of the terminal base or connector block. This method of software
cold-junction compensation is sufficient for applications in which
temperatures are fairly stable and uniform across the system.
06-29-2007 11:17 AM