Thanks for posting on the National Instruments forum.
Have you checked if all the softwares a well installed on your target? In MAX, you explained that you can see you PXI target, so may you click on the software menu:
and then click on the "Add/Remove software" button to install all the softawres on your target. (It's recommanded to previously uninstall those already on the target).
After this checking and/or install, does it work?
Regards,
06-09-2008 01:49 PM
Matthias Baudot | Software Architect | Founder at STUDIO BODs
06-16-2008 03:33 PM - last edited on 03-14-2024 10:13 PM by Content Cleaner
Hello everybody.
The problem is solved ! The reason of my problem is that LabView RT 8.5.0 does not support more than 2GB RAM installed on the computer, like it's describe in this document.
Adjusting my RAM to GB permits the things that were not possible before :
- to connect the target in a LabView Project and deploy some code.
- to active the multiple core processor in the BIOS of the machine
I precise that removing the USB keyboard is useful. Indeed with my keyboard plugged, when I install additional software like VISA Server for example, MAX do not recognize the target automatically, I have to add it manually specifying the IP address, and I cannot connect the target in a LV Project.
Unplug the USB keyboard (and all other devices) solve this problem.
Have a nice day...