I am working on a project that involves a decent number of double and boolean shared variables. The alarms and data need to be logged. By setting the resolution of double SVs, I have manged to control the amount of data logged. However, I am not yet able to handle the issue of boolean data types. (These indicate ON/OFF state of various components). I just want to log data points on value change. As I am new to DSC 2017 any suggestion would be helpful
Another small question the scf file format used in earlier DSC versions. Is it also available with DSC 2017?
Regards
Solved! Go to Solution.
12-11-2021 08:13 PM
Any suggestion??
12-13-2021 03:37 AM
Scf files are not supported any more but there is a migration tool (under Tools->DSC), although I never used it.
The documentation I read says nothing about how logging is optimized (if ever) for a boolean value.
My guess is that logging occurs only when values change. A small test project may give you an answer quickly.
If there is no optimization, you may consider using numeric variables instead of booleans.
12-16-2021 09:48 AM
Thanks for the reply
I converted boolean SVs to Integer but no improvement. The library has 2600 SVs, I even disabled logging of Alarms but still the problem persists. As the application runs for an hour then database size is around 1.5GB..really stuck at the moment 🤔
12-21-2021 10:36 AM
By disabling the generate event on value change property on the ALARMING page I have managed to address the database size problem, the alarms are logged and retrieved fairly efficiently; so a big step forward. However, despite logging being enabled I am unable to see any data in Citadel.
Are there any special setting for logging data for boolean shared variables.
12-22-2021 09:25 AM
SOLVED: the logging option was unchecked for most SVs.
By disabling the generate event on value change property on the ALARMING page the database size remains manageable.