Can you give us some more info about what you are publishing?? One register, two, three, a hundred. Modbus is usually limited to 100 registers per read or write command (maybe 125). Are the variables in consecutive order or spread all over the place?? How many devices are reading this data?? Show us some code.
One other thing, are you sending RTU or ASCII formatted data?? ASCII is twice as slow.