01-11-2009 08:29 PM
For one of the application we need to choose a hardware(switch matrix) so that we can switch over 120 different inputs.
We are using Digital Multimeter for the measurements of these inputs.
But i stucked on how to select good combination of switch matrix.
Please give me advice.
01-12-2009 08:11 AM
Hi adat,
I advise establishing a set of switching requirements for your application. I've provided a list of specifications and features that you can use in determining the requirements for your application:
Bus Type (PXI or SCXI)?
OS Support (Windows XP, Vista, Linux, Real-Time, etc.)?
Switch Type (External Relay Driver, General Purpose, Matrix, Multiplexer, RF, etc.)? - Matrix or Multiplexer
Relay Type (Armature, Reed, FET, Solid State, etc.)?
Connection Speed (Scan Rate, Actuation Time)?
Measurements to Perform (Type, Accuracy, Resolution, etc.)?
Maximum/Minimum Voltage?
Maximum/Minimum Current?
Maximum Power?
Maximum Bandwidth?
Crosspoint/Channel Density? - 120 Channels
Maximum Number of Chassis Slots?
Module Mating Connector Type?
Relay Lifetime?
Answer as many of these questions as you can, and we'll be able to assist you further.
Thanks and best regards!
Chad Erickson
Switch Product Support Engineer
NI - USA
01-13-2009 07:50 AM
Hello Chad,
Thank you very much for your valuable reply.
Please find remarks in Blue for more info.
PXI.
Windows XP.
Multiplexer.
Electromechanical relays,latches.
100 cycles/s & 10ms.
Need to measure voltage drop across resistive loads by using DMM.
Maximum: 0-100V, Minimum: 0-12V.
Maximum: 0-100mA Minimum:0-1.2mA.
Maximum Power?
10W Maximum.
Maximum Bandwidth?
Not sure.
10 maximum slots.
Please advice for mating connector. we already chosed NI TB-2636 terminal block.
Relay Lifetime?
1000000 cycles.
Waiting for you reply friend!
Thanks & Regards,
Adat.
01-13-2009 09:06 AM
Hi Adat,
I recommend the NI PXI-2575. If for some reason this module is unusable, the NI PXI-2527, PXI-2529, and PXI-2576 could also be suitable for this application. Here are the specifications for the NI PXI-2575:
Please find remarks in Blue for more info. Added remarks in Red.
Bus Type (PXI or SCXI)? PXI. PXI.
Windows XP. Windows XP.
Multiplexer. Topology can be configured by software to be a 1-wire 196 × 1, 2-wire 95 × 1, or 2-wire 98 × 1 Multiplexer.
Electromechanical relays,latches. Electromechanical, latching relays.
Scan Rate Benchmark w/ NI PXI-4071 DMM: 105 cycles/s (4.5 digits of resolution, 10 V range), 100 cycles/s (5.5 digits of resolution, 10 V range) DevZone Document with benchmarks attached: NI PXI-4071 - DC Voltage - DMM/Switch Handshaking Scan Rates
Actuation Time: 1 ms (typical), 3.4 ms (max)
Measurements to Perform (Type, Accuracy, Resolution, etc.)? Recommended for switching voltage.
Maximum/Minimum Voltage? Maximum: 0-100V, Minimum: 0-12V. Maximum:100 V CAT I, Minimum: 10 μA @ 10 mV.
10W Maximum. 30 W, 37.5 VA.
Not sure. 20 MHz.
196 (1-wire) or 98 (2-wire). 10 maximum slots. Each module fits in 1 PXI slot. If a 1-wire configuration is used, only 1 slot is required.
Please advice for mating connector. we already chosed NI TB-2636 terminal block. Advised connectivity is either: a) the LFH200 to Bare Wire Cable Accessory, or b) the LFH200 to 4 50-Pin DSUB -S (CH-CH Twisted) Cable Accessory and 4 x TBX-50 Connector Blocks.
1000000 cycles. 2500000 cycles (10 VDC, 100 mADC resistive).
Hope this helps!
Chad Erickson
NI - USA