05-22-2012 01:44 PM
Trying to make differential measurement of the voltage drop of a low side current shunt to monitor battery current.
The battery is isolated from the cRIO NI9205 measurement common. Is it necessary to add a 100k resistor to common to ensure that my common mode is within spec's.
What measurement accuracy would you expect if a 0.2% shunt resistor was used ?
05-23-2012
09:57 AM
- last edited on
05-06-2025
09:51 PM
by
Content Cleaner
Hi Brooks,
I believe you would need a bias resistor when taking dfferential measurements. Please refer to our Field Wiring Guide for a more detailed explanation as well as diagrams. Also, measurement accuracy is dependent on the input range. A table of this can be found in the 9205 user manual.
05-24-2012 04:38 AM
Some remarks to the accuracy:
Tempco of the shunt? The current will heat up the resistor and the value will change ....
The absolute value of your shunt can measured by a calibration...
I hope you use 4 wire technique
If you are not only measuring a DC current the impedance of the shunt is important. ( inductivity and capacity ... yes even a shunt can have a resonant frequency 🙂 )
Usually the datasheet of the shunt will give you an answer.