Stairstepping in thermocouple data with TC-2095/SCXI 1102c

Here's my setup:

 

32 K-type thermocouples (mixture of grounded sheathed and ungrounded exposed tip)

TC-2095 rack mount thermocouple connector block

SCXI 1102c module

 

I am having an issue of stairstepping in the thermocouple data I am getting.  The system seems to be sampling at the 500-1000 Hz sampling rate because noise and gentle sloping is recorded in the tc data in between the major jumps in temperature.  The stairsteps generally occur at 1 or 2 Hz.  The only thing I modified on the hardware was swapping in the 10 Mohm resistor packs into the tc-2095 to prevent a grounding issue from ruining the readings from our grounded thermocouples.  Any thoughts on how to fix the stairstepping?

 

Thanks,

Alex

0 Kudos
Message 1 of 2
(5,696 Views)

Hey,

 

Did this work without the10Mohm resistor pack?? Did this ever work?  

 

You say you have grounded thermocouples---what are they grounded to?  Can you expand on this setup.

 

How did you configure the dip switches on the TC-2095 for each thermocouple? I'm referencing the settings mentioned in table1 of the tc-2095 specifications sheet.  This is found on page 5-6 of thespecs manual: http://www.ni.com/pdf/manuals/321731b.pdf

 

Can you attach a screenshot of the data that you are seeing so that I can inspect it.  Also what sampling rates are you specifying?  how are you programing this (Labwindows/labview?? etc... )

 

Please post back with this info so we can work to resolve this issue thank u

Charley Dahan