SCXI-1120 temperature limited to 106 C

I'm using a SCXI-1120 with a 1320 and the PCI-6031E. The TC is type J. The MAX is set at 2000 gain along with the 1120 module. I'm back to using the 1120 Thermocouple VI from LabVIEW ver 6.1. A test box was made to input mV into the 1320 while monitoring it on a Fluke 52II Thermometer to verify calibration. The chart reads accurately up to 106C where it flat-lines. I need to measure a range of 20 to 500C. What have I overlooked here?

wAllenr
0 Kudos
Message 1 of 2
(2,610 Views)
Found the answer, I was multiplying gain not dividing.