Company: Max-Planck-Institut für Plasmaphysik, Garching, Germany
Author(s):
A. Sigalov, N. Arden, H. Eixenberger, L. Giannone, C.-P. Käsemann, M. Schandrul, K.-H. Schuhbeck, G. Sellmair, B. Sieglin, W. Suttrop, M. Rott, W. Treutterer and the ASDEX Upgrade Team
Max-Planck-Institut für Plasmaphysik, Boltzmannstraße 2, 85748 Garching, Deutschland
W. Zwick, National Instruments, Ganghoferstraße 70b, 80339 München
NI Product(s) Used:
cRIO (NI-9038, NI-9064, NI-9149), C Series Modules (NI-9205, NI-9425,
NI-9242, Ni-9227, NI-9375, NI-9469), LabVIEW software and LabVIEW FPGA module.
Industry:
Innovative Research, plasma pysics
The power supply of the fusion experiment ASDEX Upgrade in Garching nearby Munich based on three flywheel generators has expanded with additional equipment over the years. The reliability and accuracy of the old supervisory system could no more cope with the increased complexity.
The energy for ASDEX Upgrade, Germany’s largest experiment for nuclear fusion research of the Tokamak type, is provided by three separate networks based on flywheel generators. They can supply an electrical power up to 600 MW for a time period of about 10 seconds [1]. The permanent refinement and required flexibility, characteristic to a basic research project, lead to a continuously increasing hardware complexity, which also has to be supervised.
Different supervisory systems ensure a safe operation of the generators. To increase the reliability and accuracy, the old supervisory system, which was based on conventional hardware, has been replaced step by step by a new distributed embedded system from National Instruments (Fig.2). Measurement, digitalization and data processing is now done close to the signal source, increasing the measurement accuracy. The recorded signals are stored locally, making the whole system more stable and independent from the network performance. The data is also used for online monitoring by some cRIO and PXI systems which are linked via Ethernet.
The monitoring and data acquisition of the generators and of some installations of the power supply are based on distributed system architecture. [2] (Fig.3). All systems have the same sampling rate (10 kHz) and are controlled by an external trigger. The implemented NI-Hardware communicates internally over Network-Streams and with the external systems (e.g. SIMATIC) over OPC-Server and UDP Protocol. The measured data is saved locally on the own hard disk and simultaneously transmitted to a Windows-computer for real-time display. The file transfer for archiving is done by WebDAV-Protocol. A total of more than 350 channels are stored.
The real-time-computers have the following functions:
COI has a controller PXIe-8135 and three multifunction data acquisition cards PXI-6259. It serves to data acquisition for the COI converter for fast plasma control, which consists of two similar anti-parallel four-quadrant-converters, each one with a forced-commutation thyristor-based DC-switch. The installation is fed by 10,5 kV/85-110 Hz, with a pulsed power of 14MW and a nominal DC output current of 27 kA for each converter [3].
L5E is a CompactRIO system with 2 modules for analogue measurements of the high current converters for supplying the magnet coils of the experiment with a pulsed power of 580 MVA and current up to 45 kA/10 s.
MAZ includes a PXI-Chassis with 12 PXI-6143 cards and serves for the simultaneous measurement of the magnetic probes over 96 channels. This chassis is connected over a MXI-cable with a LabVIEW-computer.
EZ4 consists of a CompactRIO Chassis with a cRIO-9038-controller (Fig.4). It captures and monitors the electrical parameters of the flywheel generator EZ4.
Modules of the C-Series with Delta-Sigma-Analogue-Digital-Converter are used for the direct measurement of currents and voltages of the transducers (measuring transformers). The 4th order elliptical filter (Cauer) implemented in the FPGA has a very steep transition in the transfer function. For the filter design LabVIEW Digital Filter Design Toolkit was used. The obtained values are used for the calculation of important generator parameters: active and reactive power, thermal stress, stored mechanical energy and consumed electric power. The optimized calculation of these values in the FPGA is realized with LabVIEW FPGA IP-Builder. When stipulated limits are exceeded the system will, by the help of safety loops, trigger a premature pulse end respectively an immediate pulse stop of the experiment and will report the reason. A deterministic connection between cRIO and the Linux-computer for fast control of the plasma discharges (4 in Fig. 3) is realized by fiber optic cable. For this purpose the 4B/5B signal coding is implemented in the FPGA, transmitting data together with control symbols.
In difference to the event triggered data acquisition, the monitoring system runs continuously. In order to synchronize these two systems, a procedure as shown in (Fig. 5) is implemented.
By the trigger-based measurement a predefined number of measurement points (e.g. 3000) will be read between A and B. By the continuous measurement the trigger appears within the measurement interval (Point A). The necessary 3000 measurement points, starting from the trigger (event), will be in this case accessible only at time point C. They will be taken from two consecutive intervals of the continuous measurement between points A and C and will be synchronized. Should no data be available after a Timeout, then the system continues to run without this data.
The basis of visualization consists of the dynamic generation of Queues, which allows the operator to decide himself how many graphs are opened and how many curves should be displayed in each graph. The following tasks shall be solved:
The number of necessary visualization points is reduced dynamically by Max-Min-Decimation [4, 5]. The peak values are displayed on the graph despite the strongly reduced data. This algorithm increases the speed of visualization without loss of the peak values.
The distributed system architecture as implemented by using the NI solution brings the following benefits:
The flexibility of the NI solution can accommodate unique applications such as our system. We could so solve the problems of a very complex and expensive system with a reasonable investment and time.
Acknowledgement This work has been carried out within the framework of the EUROfusion Consortium and has received funding from the Euratom research and training programme 2014-2018 under grant agreement No 633053. The views and options expressed herein do not necessarily reflect those of the European Commission.
[1] C.-P. Käsemann, E. Grois, F. Stobbe, M. Rott, K. Klaster and the ASDEX Upgrade Team (Max-Planck-Institut for Plasma Physics): Pulsed Power Supply System of the ASDEX Upgrade Tokamak Research Facility. Environment and Elektrical Engineering (EEEIC), 2015 IEEE 15th International Conference on. Date of Conference: 10-13 June 2015. Page(s): 237-242. ISBN: 978-1-4799-7992-9
[2] The Rise of Distributed Systems – Weshalb verteilte Systemarchitekturen immer öfter zu finden sind. National Instruments. 15.Okt.2014. http://www.ni.com/newsletter/52383/de/
[3] Alexander Sigalov, H Eixenberger, C -P. Käsemann und das ASDEX Upgrade Team:
Datenerfassungssystem des Vierquadranten-Stromrichters für die Plasma-Lageregelung von ASDEX Upgrade. Virtuelle Instrumente in der Praxis 2014 (2014), S.6-9
[4] How to Graph "Big Analog Data" or Large Data Sets Efficiently. http://forums.ni.com/t5/Example-Program-Drafts/How-to-Graph-quot-Big-Analog-Data-quot-or-Large-Data-.... 27.01.2017
[5] What Type of Decimation Algorithm Does LabVIEW Use to Display Data on a Graph? http://digital.ni.com/public.nsf/allkb/f694ffeea0acf282862576020075f784 29.07.2009
Alexander Sigalov
Engineer scientist
Department E1/L6
Tel. +49-89-3299-1647