Hi all,

I have the same phenomenon with http://forums.ni.com/t5/Real-Time-Measurement-and/cRIO-Connects-then-disconnects/td-p/1884039 and http://forums.ni.com/t5/Real-Time-Measurement-and/cRIO-9073-Disconnects/m-p/1751378#M10637 .

 

But my hardware is sbRIO 9606. Can i use this method, " install the latest version of NI-TimeSync to the cRIO and PXI found here: http://joule.ni.com/nidu/cds/view/p/id/2819/lang/en" , to solve the problem?

 

Thanks a lot!!! 

0 Kudos
Message 1 of 3
(4,841 Views)
Solution
Accepted by topic author iDeam

It is possible that the same recommendation would solve your problem as it does affect sbRIO boards as well.  The issue is very specific though and only afffects boards with a static IP address defined, running NI-TimeSync 1.1 with some other settings.  If you're using a static IP address on your 9606 and have NI-TimeSync 1.1 installed, I would definitely recommend upgrading the version of NI-TimeSync on your host PC and then on your 9606.

Alex Person
NI-RIO Product Support Engineer
National Instruments
0 Kudos
Message 2 of 3
(4,825 Views)

Thank you!!

After i updated to 1.1.3, the problem was solved.

0 Kudos