03-05-2009 02:46 PM
The cRIO 9101 shows a com port in MAX but the port settings are disabled.
The manual doesn't have any information about the serial port (DB9 connector).
What needs to be done to enable it and can it be used to commnicate to a device from a host computer?
Thanks,
Steve
03-07-2009 09:54 AM
Hi Steve,
The 9101 is a chassis and not a controller. I assume you are trying to communicate with a controller serially. What controller is it? And what are you exactly trying to do?
03-09-2009 08:49 AM
The controller is the cRIO-9014 and it's connected to the chassis along with NI-9211 modules for monitoring temperature.
The intention is to send Modbus commands from the cRIO's RS232 port to a Watlow (temperature) controller in order to set the temperature setpoint on the Watlow controller based on the temperature from the 9211 modules. In addition the setpoint and any CRC errors would be sent back through the cRIO's RS232 port to be read by the host computer.
There appears to be a modbus RTU IO server available for this through the RT software. Was intending to use my modbus drivers but if the IO server is better I'll use that instead.
Can modbus commands be sent through the cRIO's RS232 port for controlling and reading a Watlow controller and would the IO server be better to use?
Thanks for the help
Steve
03-09-2009 09:04 AM
You should be able to do this.
You would require both the LabVIEW Datalogging and Supervisory Control (DSC) and LabVIEW Real-Time. Refer to How to turn a RT Target into a Modbus Slave using IO Servers for more information on setting up a RT Target as a Modbus Slave device.
If you don't have LabVIEW DSC, you could probably get the whole thing to work using the LabVIEW Modbus Library, but I am not familiar with the library to answer questions on it.
03-09-2009 09:14 AM
Just one more question-
Why is this COM port disabled in MAX if the cRIO RS232 port is for Modbus communication. See enclosed jpeg image.
Thanks,
Steve
03-09-2009 09:34 AM
03-09-2009 10:56 AM
Hi Steve,
The COM port is not supposed to show up as disabled. Please check whether NI-VISA is installed properly on both your RIO as well as your computer.
Ipshita C.
03-09-2009 11:06 AM
Steve,
Actually, this behavior is by design. We do not support changing the port settings for a COM Port on a cRIO using NI-MAX. You will need to use the VISA Config Serial Port VI Adnan mentioned in his post. Or you can use a property node you find on the VISA Advanced pallette if you want to quickly change a few settings.
Pankaj
03-09-2009 12:12 PM
Pankaj,
Does that mean the only was to communicate through the cRIO com-port is from a Host.VI (in a project).
A VISA resource name (visa://NI-cRIO9014-013DBB8D/ASRL1::INSTR) for this cRIO com-port can be made in the host VI of an FPGA project but doesn't seem to be allowed in the target FPGA.VI (that's compiled).
Enclosed is my project. Currently it only reads temperature from the 9211 modules.
Thanks very much to everyone for the quick responses.
Steve
03-09-2009 05:34 PM
One of the things that might be different is that when you are targetting the COM port on the controller from a VI running on the host, you have to indicate that it is a remote VISA resource, and hence you use visa://hostname/... as a prefix. For a VI running on the target itself, the COM port is a local VISA resource, so the resource name would just be "ASRL1::INSTR". I don't know if I answered your question, but do let me know if you need more information or if you have other questions.
Pankaj