A problem in debugging sbRIO-9627 and REM-11178.

Solved!
Go to solution

Hello everyone, I have a problem in debugging sbRIO-9627 and REM-11178. Because of the limitation of space and weight, I can only use sbRIO.The data manual states that rio must have two network ports to control REM-11178. I can't control REM-11178 through figure 1. I also found that cRIO-ECAT-S can expand the network interface. I want to know if I can control REM-11178 through figure 2.Thank you very much.question.png

 

0 Kudos
Message 1 of 3
(1,819 Views)
Solution
Accepted by topic author uestcer07

Hi uestcer07,

 

I am afraid that you can't use the figure 2 to control the REM-11178. Because the cRIO-ECAT-S, in fact, is a slave. And if you want to use the EtherCAT protocol, the master must have two network ports at least.

 

Thanks!

0 Kudos
Message 2 of 3
(1,764 Views)

I really appreciate your help very much