Real-Time Measurement and Control

cancel
Showing results for 
Search instead for 
Did you mean: 

9208 Active Measurement

Solved!
Go to solution

I apologize upfront as I see there are several threads on this topic, but unfortunately, I'm not grasping them terribly well for my application.

 

I just purchased a couple 9208 spring terminal modules for a cRIO.  I have four instruments. Two are passive loop to which I supply power, and two are active loop in which the instrument is supplying the loop power. One 9208 is for the passive loop, the other is for the active loop.

 

There are six sensors (4-20mA) assigned to each card. The six on the passive loop 9208 are all reading the correct output signals when test signals are sent to each of the six channels. These are wired with a (my) 24V PS, positive connected to the Vsup in one location. I connect the COM on this setup to the negative post of the PS.

 

For the other six on the other 9208, the instrument/sensor itself is supplying the loop power. I've connected the positive lead from the instrument to the Vsup, and the return/negative lead to the AI terminal for each channel. I am not reading anything and have verified the test signal output from the instrument with a multimeter.

 

I previously had a multifunction input card measuring this signal and was able to verify the output test signals. I think this is confusing me as I think I should be able to measure the current with the two wires coming from the instrument.

 

I don't think the module is bad because it is recognized by the cRIO and LV... but I don't know.

 

Any help is appreciated. Since I was able to read it with the multifunction IO card with two wires, I figured this would be just as straightforward on the active loop.

 

Thanks.

0 Kudos
Message 1 of 7
(2,058 Views)

Please share a simplified connection diagram for both cases.

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution
0 Kudos
Message 2 of 7
(2,024 Views)

I believe late last night I've arrived at the correct solution but would appreciate a review.

 

I've attached the wiring diagram that I'm using for both of the 9208 measurements (passive vs active). In this configuration, I am able to measure both instruments correctly and they correctly respond to the test signals sent from the instrumentation. I think my hangup was using the COM terminal. I thought I might have to bridge the COM and VSUP terminals for the non-powered (powered by the instrument) measurement, but I wasn't sure.

 

Anyway, thank you for your help and review/correction.

0 Kudos
Message 3 of 7
(1,999 Views)
Solution
Accepted by topic author quarterlbr

You don't need to short the COM and VSUP in a powered case. Connect your active instrument between AI and COM.

santo_13_0-1781191022764.png

 

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution
Message 4 of 7
(1,996 Views)

Thank you very much for the prompt reply.

 

So, I should have detailed that I have three signals coming back from two different instruments (actually all four have three separate signals on a wire pair back to the cRIO). All signals are provided in pairs. I assumed I needed to connect both wires to somewhere on the 9208. That's why I shorted the COM and VSUP, to use it as a bus.

 

Does it hurt to have VSUP jumpered to COM? If not, is there any downside to the way I wired it?

 

Do I only need to connect one wire from each instrument to the COM and the other leads (from the other signals) remain disconnected (i.e., I only have to connect one wire)?

 

0 Kudos
Message 5 of 7
(1,987 Views)

Now, re-thinking, all VSUP lines are a bus; by connecting COM to VSUP, you created a COM bus with several connecting points.

santo_13_0-1781317277088.jpeg

About connecting only one COM from each instrument will work if the output signals aren't isolated and common referenced to the instruments' power supply. If each of the output signal were isolated, then you need to tie all the wires to COM.

Do you have more info of the Active loop instruments you're talking of? datasheet or manual link?

 

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution
0 Kudos
Message 6 of 7
(1,959 Views)
Solution
Accepted by topic author quarterlbr

Thank you for your reply. I was thinking the same thing, that I was creating a COM bus.

 

I ended up contacting NI technical support as well and the "approved" method was to do as you said originally, which was to connect all returns from the signals to the COM port(s). Leveraging the VSUP bus as a COM bus was not an option they suggested, so I went ahead and followed your (and NI's) recommendation and joined the respective wires together and connected them to the COM port on the respective card. I did provide feedback to NI that it seems a messy solution, especially if you have need for 16 different channels, to connect all 16 instrument wires to one (or two) COM ports on the card, and if you can leverage the VSUP bus as a COM bus, that would be much cleaner (and simpler to understand).

 

It ended up working (apparently anyway) the same both ways: with all wires joined and connected to the COM terminal(s) directly, and also with one COM and one VSUP terminal shorted and connecting each instrument signal wire to the AI and adjoining/paired VSUP terminal port.

 

I didn't want to risk damaging the card by leaving my original solution in place (though I'm not sure how damage would occur), so I fell back on your original suggestion, which again was the one NI suggested as well.

0 Kudos
Message 7 of 7
(1,912 Views)