RT scan engine mode goes into configuration mode when error 66464 happens.

Hello, 

 

I'm using RMC-8354 and sometimes error 66464 happens and scan engine mode goes into configuration mode, however when I reset RT, it turns active mode again. I'm using several RMC-8354 servers but only one RT shows this error. I suspect this is uniquely from only one RT. I already googled and what is the meaning of error 66464. What I do know is how to fix it. not just information. I contacted some channels but answer was not okay to me. Please give some ideas of this problem. Thanks in advance!!

Best Regards,
-----------------------------------------------------------------------------------------------------------


0 포인트
1/4 메시지
2,026 조회수

Hi  gooohestpoo,

 

Have you tried comparing the software installed on a normal system with the software on the problem system?

As you know, error 66464 can happen when the iteration period of NI scan engine is changed.

I think checking the configuration of the system is a good start point to resolve it.

 

Thanks

 

0 포인트
2/4 메시지
2,009 조회수

Hi Chan82,

 

Thanks for your response. 🙂 I checked installed software series from MAX compare with other RTs, but couldn't find any specific weird one. I guess this is not the root cause right now. 

Thanks for your comments anyway.

Best Regards,
-----------------------------------------------------------------------------------------------------------


0 포인트
3/4 메시지
2,002 조회수

Hello,

 

This is a description of error 66464.

 

The global time on the controller was altered, which might affect the period of an iteration of the NI Scan Engine. A timing source such as IEEE-1588 or GPS modified the global time value on the controller. This can result in a temporary phase shift, which would alter the update period for NI Scan Engine variables for one iteration.

 

Please check the time of the controller time.

 

Regards

0 포인트
4/4 메시지
1,987 조회수