04-04-2019 08:04 PM
Hello,
I'm using RMC-8354 and sometimes error 66464 happens and scan engine mode goes into configuration mode, however when I reset RT, it turns active mode again. I'm using several RMC-8354 servers but only one RT shows this error. I suspect this is uniquely from only one RT. I already googled and what is the meaning of error 66464. What I do know is how to fix it. not just information. I contacted some channels but answer was not okay to me. Please give some ideas of this problem. Thanks in advance!!
04-05-2019 12:05 AM
Hi gooohestpoo,
Have you tried comparing the software installed on a normal system with the software on the problem system?
As you know, error 66464 can happen when the iteration period of NI scan engine is changed.
I think checking the configuration of the system is a good start point to resolve it.
Thanks
04-05-2019 01:00 AM
Hi Chan82,
Thanks for your response. 🙂 I checked installed software series from MAX compare with other RTs, but couldn't find any specific weird one. I guess this is not the root cause right now.
Thanks for your comments anyway.
04-08-2019 01:01 AM
Hello,
This is a description of error 66464.
The global time on the controller was altered, which might affect the period of an iteration of the NI Scan Engine. A timing source such as IEEE-1588 or GPS modified the global time value on the controller. This can result in a temporary phase shift, which would alter the update period for NI Scan Engine variables for one iteration.
Please check the time of the controller time.
Regards