04-28-2022 10:18 AM
We have a PXIe-1088 chassis with a PXIe-8880 controller currently running PharLabs as OS. On our host we updated LabView+Veristand from 2019 to the most recent version (2021 R2). We updated the drivers on the PXI-target accordingly but the VeriStand RT Engine is missing and it cannot be installed (it does not appear in MAX when clicking on "add/remove software"
I would appreciate feedback how to solve this problem.
P.S. We noticed two things:
* The installed LabView application is a 32bit application while VeriStand is 64bit. In the past we made the experience that 64bits together with RT-targets does not work very well!
* Could this issue be linked to the OS which is PharLab which might not be supported anymore?
Solved! Go to Solution.
05-06-2022 04:55 AM
In fact, it turned out that the problem arises due to the fact that PharLabs is not supported anymore:
05-06-2022 04:59 AM
For those who have the same problem and need to replace PharLabs here some notes about how I did this:
Update BIOS:
Replace OS on Target:
Install Base Image:
Next problem: The target boots and I can find it via MAX but since it boots in safe mode I cannot install any software! I get to the login window where I enter "admin" and "{password}" to login. But then I get a message that no software can be installed when the target is in safemode. So I try to follow the "offline installation guide" here: Installing Software to Offline NI Linux Real-Time Targets - NI. I followed the instructions and tried this a couple of times but either the "install software" option was disabled or MAX had issues to find the RT target. I was also puzzled by the screenshot of the instruction where it looks as if the target is not connected while installing the software (therefore the red x on the target). However, at some point it worked. This was the following situation
From there on I simply followed the description and completed the base image installation.