03-16-2018 09:21 AM - edited 03-16-2018 09:38 AM
I've implemented NTP on a sbrio-9651 using the guidance in NI NTP Guide and it seems to work. I then tested the behaviour by deliberately changing the clock. To monitor the hardware I broadcast a CAN message with a counter value to see whether the Real Time processing was interrupted at any point.
My findings were;
As an aside I performed a different Test looking at the step change of 4min 5 sec to the future. I logged the Timed loop duration counters which 9 out of 12 showed a pause of 50 second delay at the moment the clock was changed.
So my question is; Is it possible to configure the Timed Loops to use MONOTONIC clock and not be affected by the NTP Time sync?
There is a similar discussion here: Permissions Setting date time with system exec or script
Background Reading
03-19-2018 10:11 AM - edited 03-19-2018 10:13 AM
I've just found this knowledge base article about getting unexpected Timed Loop behaviour when time is set backwards: https://knowledge.ni.com/KnowledgeArticleDetails?id=kA00Z000000P9pJSAS.
Is this issue still current?
03-19-2018 10:43 AM
Oliver_15,
What version of LabVIEW are you using? This is a known issue that has been resolved in LabVIEW 2015 SP1. If you are using LabVIEW 2014 or 2015, the only workaround is to reboot the controller immediately after changing the time.
For more information you can reference, LabVIEW Run-Time Hang On NI Linux Real-Time After System Time Set Into Past.
Andy
Product Support Engineer
03-19-2018 11:11 AM
Hi Andy,
I'm using LV2015 SP1 (Version 15.0.1) 32bit Environment so doesn't quite make sense.
The sbRIO-9651 has;
03-19-2018 11:53 AM
Hey Oliver_15,
Interesting. Did you upgrade this controller from a previous version of software or have previous NI drivers installed on the host computer? Could you provide a MAX Technical Report for the host and the cRIO? This should help us understand the software stack where we are still seeing this behavior.
You could try reformatting the target via MAX to ensure the necessary updates for the fix are on the controller.
03-19-2018 12:22 PM
Hi Andy,
This controller had v3.0 firmware before I updated it. I've also got LV2015 SP1 in 32bit and 64bit, as well as NI Max v17.0.0f0 installed. Attached is a MAX report of the software stack.
I'll try reformatting the sbRIO and see if that helps.
03-19-2018 02:57 PM - edited 03-19-2018 02:57 PM
Hi Oliver_15,
After a little more investigation, I think you may be seeing a related issue to the one mentioned above that was found and resolved in LabVIEW 2016 (CAR 567981). This is specific to Timed Loops hanging when the time is changed during execution. This looks to be the exact behavior you are seeing. I recommend testing your code in LabVIEW 2016 to confirm that this is the cause.
Andy
07-19-2018 10:54 AM
- Setting time to the past
- 6mins - CAN message counter froze - I suspect the Timed loop stopped executing.
- 20secs – Adapted with no issues.
*FACEPALM*, they use the wrong clock. Yet another case of not having read the manpages.
man 3 clock_gettime
Actually, I'm regularily seeing such things in old industrial companies, especially in regulated areas like medical devices or automotive.