Multifunction DAQ

cancel
Showing results for 
Search instead for 
Did you mean: 

cDAQ 9265 Increased Output

Hello,

 

We are using a 9265 to for a 4-20mA device. It both powers, and controls the device. 

 

We want to use a 9203 to read back the 4-20mA command. 

 

The issue is, the device has approximately 550 ohm impedance, plus the 130 ohm impedance of the 9203, puts us over the maximum 600 ohm of the 9265, and compliance voltage of the 9265 isnt enough to push a full 20mA to the device.

 

We have other ways to read it back, but my concern is, how future proof are we? If we have a new device that requires more power, and compliance voltage of the 9265 isnt enough, we wont have any other options for control? (Other than another standalone loop calibrator).

 

So, is there a more powerful 9265?

 

Thanks

0 Kudos
Message 1 of 3
(811 Views)
0 Kudos
Message 2 of 3
(727 Views)

Unfortunately all the C Series current output modules can drive only up to 12V which means you're limited to only 600ohms load.

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution.

Finding it hard to source NI hardware? Try NI Trading Post
Message 3 of 3