What if using 12V to USB-6501 or USB-6002 's digital input port
Hi there,
I am a vehicle test engineer。I'm going to buy DAQ test equipment for the company。
Gentlemen, please answer the following questions for me.What if using 12V to USB-6501 or USB-6002 's digital input port?
12V is often used in vehicle specification product development,I read the product manual. The input voltage range is 5V, but I also noticed that there will be voltage protection. I want to use this device to distinguish the digital logic level of 0V and 12V. 0V is 0 and 12V is 1. I want to know whether connecting 12V to the digital port for a long time will damage the equipment.
---------------------------------------------------------------------------------manual  of 6002 said-----------------------------------------------------
Input voltage protection ............................................................................±20 V on two lines per port (maximum of five
lines for all ports) for up to 24 hours
best regards
(1,248 Views)
Accepted by topic author Zion1024
Yes, it will damage the device beyond recovery or even beyond repair.
These are 5V logic level compatible Instruments and for example, 6501 specification states not to exceed 5.8V on digital inputs.
In terms of your voltage threshold to detect a logic high or low, it is as below,
This should be interpreted as any signal between -0.3V and 0.8V are detected as Logic Low and anything between 2.0V and 5.8V are interpreted as Logic High.
If you are still inclined to use this hardware you can use optocoupler or logic level translators between the instrument and your 12V system.
Something like this - https://www.omega.com/en-us/data-acquisition/signal-conditioners/din-rail-signal-conditioners/p/DR-I...
Santhosh
Soliton Technologies
(1,212 Views)
Thank you for the idea of optocoupler!
Please allow me to ask for more, In Analog input condition,6002 seems to be able to withstand 12V directly for long time (less than 24hours) test ? is it right?(Of course, the maximum read value is 10V)
And,Is there any other low cost equipment(best with USB) that can directly handle with 12V signal?
(1,199 Views)
Any voltage rating beyond typical operating is dangerous for the instrument. I would not connect anything beyond 10V to the Analog Inputs.
I would suggest USB-6525 for the 12V Input/Output application.
https://www.ni.com/en-us/support/model.usb-6525.html
Santhosh
(1,173 Views)
Okey、thank you for reply
(1,138 Views)
