03-21-2013 01:57 PM
I have two types of sensors I am trying to interface to a NI 9205 AI card. One signal has a differential output (Ext +, Ext -, Sig +, Sig -) and the other has referenced output (Ext +, Sig +, Comm). I have connected the Ext +, Sig - and Comm to the Comm on the NI 9205 card. Also, the exctitation power Pwr - for both types of sensors is connected to the Comm. The MAX configuration for all the sensors is RFSE. Only the referenced output sensors are reading and the Diff signals are zero. What do I need to do to mix both types of signals on the NI 9205 card?
03-21-2013 02:26 PM
You setup the DAQ termination on a channel basis. You can have some be RSE while others are Differential.
03-21-2013 02:41 PM
How about the physical connection?
03-21-2013 03:04 PM
For the differential inputs, the inputs are actually 2 channels on the DAQ. They are usually in groups of 8. So AI0 setup as a differential will have the positive of the signal going to AI0 and the negative going to AI8. Lookup your DAQ card to make sure.