07-03-2022 09:02 AM
大家好,我最近在使用C++编程对NI9184+NI9260产生连续的台阶波形。用示波器测试9260实际输出波形如附件图1所示:在台阶切换之间,会有一个归零的过程,这个归零是我不希望有的过程。为了排除我这边软件的问题,我用NI MAX测试:先产生一个正弦波,停止后重新产生,也会出现如图2所示的归零过程。
上面的过程简单总结为:启动生成任务,停止后会保持当前值,但是再次启动,会有短暂时间变成0.
我猜想这款设备默认重新启动任务有个归零的操作。那么有没有什么方法在重新启动任务时不要这个归零操作呢?另外,还没有什么方法在不需要重新启动任务,可以实现我这个台阶波形产生呢?顺便说下:我的应用是需要连续输出信号,变化速率很慢,但是持续时间可能达到2天以上,之前想用单个任务,可能会挤爆内存
07-04-2022 01:04 AM
Yes, if your rate of voltage change is slow, you can skip configuring sample timing and use software timed, just start the task only once and whenever required write 1 sample to the task and only stop the task after a few days once all your work with the task is done.
07-04-2022 10:51 PM
Santhosh,
Thanks for your reply. If we do not configure sample timing, an error will occur. Some errors are as fellows:
Write cannot be performed when the auto start input to DAQmx Write is false, task is not running, and timing for the task is not configured or Timing Type is set to On Demand.
Set auto start to true, start the task, or configure timing and specify Timing Type other than On Demand.
Task Name: _unnamedTask<0>
Status Code: -200846
Task contains physical channels on one or more devices that require you to specify the Sample Clock rate. Use the Sample Clock Timing function/VI to specify a Sample Clock rate.
You cannot specify a Sample Clock rate if Mode is set to On Demand.
Device: cDAQ9184-1E2E643
Status Code: -201087
please help to check
07-04-2022 11:49 PM
You can resolve the first error by setting the "AutoStart" parameter of DAQmxWrite API to "True".
To understand the reason behind the second error, please share the list of instrument models part of the task.