Input Signal for cDAQ9189

Hello! I am working on connecting Pressure Transducers to the cDAQ9189. I have the option to purchase pressure transducer with output of: 4-20mA, 0-5V, 1-5V, 0-10V, RS485. For some reason, I can't seem to find the documentation on the accepted (or preferred) input signal onto cDAQ9189. Any help would be appreciated - thanks.

0 Kudos
Message 1 of 4
(762 Views)

cDAQ-9189 is just a chassis. You need modules to connect your input signal.

Learn more about CompactDAQ Systems

-------------------------------------------------------
Control Lead | Intelline Inc
0 Kudos
Message 2 of 4
(754 Views)

Hello, the module we plan on using is NI 9205 with DSUB. Looking at the back of it, the specs are as follows:

32-Ch +-10V to +-200mV 16-Bit Analog Input

+-10V Ch-to-COM

60VDC CAT | Ch-to-Earth Isolation

 

Does that mean I should go with the 0-10V output signal Pressure Transducer?

 

Thank you

0 Kudos
Message 3 of 4
(462 Views)

Yes, 0-10V sensor is more suitable for NI-9205

-------------------------------------------------------
Control Lead | Intelline Inc
Message 4 of 4
(435 Views)