I want to connect a 4/20mA, 2 wire loop-powered pressure transducer to an NI 9949 RJ-50 screw terminal ... which will then connect to an NI 9237 input module.
The NI 9237 module is installed into an NI compact DAQ 9174 chassis.
I will be measuring truck air brake system air pressures from Zero kPa (gauge) up to an allowance of 1000 kPa (gauge).
The 2 wires on the transducer are identified as: + Power and + signal
I would appreciate advice on the correct terminals on the NI 9949 RJ-50 please
Solved! Go to Solution.
06-11-2015 09:07 AM
Unfortunately, it looks like you have the wrong module for this task. The 9237 is used for measuring the output of bridge based sensors (such as a strain gauge). The signals it is designed to measure are fundamentally different than the 4-20mA signal your pressure transducer outputs.
Take a look at the NI 9203, 9207 or 9208. All have at least some channels designed to take a 4-20mA current input. Then, give the team at NI a call (877-387-0015) to talk through your application and verify you're selecting the right hardware for what you want to do.
06-11-2015 10:27 PM
Hi Cody,
I'm glad that I checked before I puchased the transducer.
I know that there are 3 Honeywell TEDS pressure transducers that will match up to the NI system, however I was a bit shocked by the price.
I will search around for suitable bridge based pressure transducers.
Failing that, I will look into the purchase of another NI module.
Many thanks for your prompt reply to my question.