Hi
I have 35 X HTT Pressure Transmitter (3 wires) and NI-9205 which acquires the reading of the pressure sensor 35 X HTT as voltage. How can I convert it to bar for example?
Thanks
07-23-2024 10:42 AM
According to this data sheet, the sensor has a range of 0 to 1 Bar and an output voltage range of 0 to 10V. This makes the math easy: just divide by 10.
07-24-2024 01:35 AM
So, Is it always a linear relationship? If my sensor ranges 0 to 30 bar, first divided by 10 then multiply by 30?
Thanks
07-24-2024 06:29 AM
@alhabeeb wrote:
So, Is it always a linear relationship? If my sensor ranges 0 to 30 bar, first divided by 10 then multiply by 30?
Thanks
Unless told otherwise in a datasheet, assume linear relationship. Because the min of both the voltage and measurement, it is a simple 30Bar/10V = 3Bar/V.
07-24-2024 07:37 AM
In the datasheet:
But I didn't understand it.
07-24-2024 09:33 AM
@alhabeeb wrote:
In the datasheet:
But I didn't understand it.
These are about the internal working of the transmitter and do not care in the context of the electrical equivalents.
Treat the output signal as linear mapping to the pressure measurement range.
07-26-2024 04:25 AM - edited 07-26-2024 05:21 AM
Thanks for your response.
As you said, I should have 0.333333 (V) when I measure the ambient pressure, Should I?
I'm using ni-9205 to aquaire the out signal. I connected pin 1 and pin 3 to negative and positive, respectively to the power supply 23 (V), and I connected pin 2 to channale 0 of the ni-9205 and the negative terminal from the power supply to COM of the ni-9205 and I used differential configuration, but I got not logic voltage readings (e.g. -0.4)!
Any suggestion to solve this issue?
The photos of my devices are shown here
Thanks
07-26-2024 08:07 AM
@alhabeeb wrote:
Thanks for your response.
As you said, I should have 0.333333 (V) when I measure the ambient pressure, Should I?
I'm using ni-9205 to aquaire the out signal. I connected pin 1 and pin 3 to negative and positive, respectively to the power supply 23 (V), and I connected pin 2 to channale 0 of the ni-9205 and the negative terminal from the power supply to COM of the ni-9205 and I used differential configuration, but I got not logic voltage readings (e.g. -0.4)!
Any suggestion to solve this issue?
The photos of my devices are shown here
Thanks
Approximately 0.33V for 1 bar pressure.
Were you able to confirm the sensor outputs 0.33V using a multimeter?
In addition, please connect the AISENSE to COM on 9205 terminals.