Multifunction DAQ
Drive SSR through the AO of USB-6212
Assuming we have a solid state relay (SSR), let's say the DR2260D20V (Datasheet). The control voltage range is 4-32VDC which can be provided by the AO channels in the USB-6212. Minimum input current for on-state of the SSR is 7mA while maximum input current is 15mA. As far as I know, input current is the current that flows through the SSR input when the rated voltage is applied. The input current will varry relative to the input voltage in a non-linear way (the datasheet has the graph). Let's say that if I apply a 5VDC then the input current will be  approximately 10mA.
My question: The current rating of the AO of the USB-6212 is 2mA. Will it be possible to drive the SSR through the AO and how can I protect the DAQ card (if possible)?
Many thanks!
(838 Views)
SSR datasheet gives you the curve,
If you want to "reliably" turn it ON, at least 4V is required.
Why do you drive the SSR using AO instead of a DO? and the DO can source or sink upto 16mA
Given the IOH is between 8mA and 40mA across 0-55C, you can easily manage the minimum 7mA requirements of your SSR.
Santhosh
Soliton Technologies
(820 Views)
In all honesty, I have never worked with the DOs. Do you by any chance have an example on how to achieve, let's say, a 5VDC output using the DOs?
The application is to use the SSRs to turn on and off the mains that supply two heating elements. Below is the code I was about to use with the AOs.
(796 Views)
It is similar to your code but switched to the DO variant of each of the DAQmx VIs used.
This is a good equivalent example,
Santhosh
(781 Views)
