Dear all,

 

I am trying to connect an Hamilton pH probe to the NI-9208 module. 

The pH probe is connected to a transmitter (Arc Wi 2G Adapter BT)  and the wiring diagram is this one:

Iforire_0-1700147639352.png

So, I have done the connection like that:

Arc 2G Wifi

NI9208

1

AI0

2

COM

3

AI1

4

COM

7 and 8 are connected to a 24VDC

But it is not workin.... What did I do wrong?


Thanks a lot!!!!

0 Kudos
Message 1 of 6
(719 Views)
Solution
Accepted by Iforire

As per your transmitter it needs a power source for the 4-20mA channels.

santo_13_0-1700150173206.png

 

You must connect as per this diagram (NI-9208 will be your PCS),

santo_13_1-1700150301248.png

 

 

Arc 2G Wifi

NI9208

1

+24V

2

AI0

3

+24V

4

AI1

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution.

Finding it hard to source NI hardware? Try NI Trading Post
Message 2 of 6
(708 Views)

Thanks a lot Santosh, I'm quite a beginner in all that 🙂

Actually, that's the first thing I've tried, but it seems I did it wrong.

Also I need to connect the COM of the NI-9208 to the GND of the power source, right?


Thank you

0 Kudos
Message 3 of 6
(704 Views)

Yes, all three - sensor, transmitter and NI-9208 must share the same GND i.e., COM.

 

Depending on wiring constraints, this also works,

 

Arc 2G Wifi

NI9208

1

VSUP

2

AI0

3

VSUP

4

AI1

+24V

VSUP

GND

COM

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution.

Finding it hard to source NI hardware? Try NI Trading Post
0 Kudos
Message 4 of 6
(692 Views)

Dear all,

 

That's me again since I have some problem in connecting a Brooks Mass Flow Controller to the same NI-9208 and a NI-9266 for AO.

 

Please find below the connections for the MFC.

BrooksMFC_Connections.png

Here is what I did:

MFC Card Connection
1 NI-9266 COM0
4 NI-9208 AI1
5   +
7 NI-9266 AO0
9   -
10 NI-9208 COM-17

Is this right?

Or should I connect as for the Hamilton probes like that (as COM-17 is already connected to '-')?

MFC Card Connection
1 NI-9266 COM0
4 NI-9208 +
5   +
7 NI-9266 AO0
9   COM-17
10 NI-9208 AI-1

Connecting this stuff is definitely not my forte 😉

 

Thanks a lot,

Iforire

 

0 Kudos
Message 5 of 6
(213 Views)

@Iforire wrote:

Dear all,

 

That's me again since I have some problem in connecting a Brooks Mass Flow Controller to the same NI-9208 and a NI-9266 for AO.

 

Please find below the connections for the MFC.

BrooksMFC_Connections.png

Here is what I did:

MFC Card Connection
1 NI-9266 COM0
4 NI-9208 AI1
5   +
7 NI-9266 AO0
9   -
10 NI-9208 COM-17

Is this right?

Or should I connect as for the Hamilton probes like that (as COM-17 is already connected to '-')?

MFC Card Connection
1 NI-9266 COM0
4 NI-9208 +
5   +
7 NI-9266 AO0
9   COM-17
10 NI-9208 AI-1

Connecting this stuff is definitely not my forte 😉

 

Thanks a lot,

Iforire

 


Please create a new topic so it is easy to find in future.

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution.

Finding it hard to source NI hardware? Try NI Trading Post
0 Kudos
Message 6 of 6
(207 Views)