Analog output not zero

Solved!
Go to solution

Hello all,

 

I have a NI DAQ mx 6343 USB x series. A analog pump is connected to the analog output A0 (pin  15).

I see (measure with a volt-meter)  when i turn on the DAQ that the output goes to 1.35 volt and then to zero.

I havent started any software yet. The problem is that the connected pump starts running for a short period 

until the output value is zero again. 

 

Is this normal and how can i prevent this.

 

Regards

 Herbert Veldhuis

0 Kudos
Message 1 of 3
(1,131 Views)
Solution
Accepted by topic author VeH

Yes, it is expected as stated in the specifications and the duration is variable based on your system.

santo_13_0-1625590638705.png

santo_13_1-1625590644928.png

 

You could add a relay controlled by a DO line that will connect the signal to AO only when you run your automation and when DO/Relay is off, connect the Analog pump signal to GND.

 

Santhosh
Soliton Technologies

New to the forum? Please read community guidelines and how to ask smart questions

Only two ways to appreciate someone who spent their free time to reply/answer your question - give them Kudos or mark their reply as the answer/solution.

Finding it hard to source NI hardware? Try NI Trading Post
0 Kudos
Message 2 of 3
(1,076 Views)

Hi, thank you.

Thats a typical RTFM, but anyway now i know how to handle it.