Hello all,
I have a NI DAQ mx 6343 USB x series. A analog pump is connected to the analog output A0 (pin 15).
I see (measure with a volt-meter) when i turn on the DAQ that the output goes to 1.35 volt and then to zero.
I havent started any software yet. The problem is that the connected pump starts running for a short period
until the output value is zero again.
Is this normal and how can i prevent this.
Regards
Herbert Veldhuis
Solved! Go to Solution.
07-06-2021 11:59 AM
Yes, it is expected as stated in the specifications and the duration is variable based on your system.
You could add a relay controlled by a DO line that will connect the signal to AO only when you run your automation and when DO/Relay is off, connect the Analog pump signal to GND.
07-14-2021 01:16 AM
Hi, thank you.
Thats a typical RTFM, but anyway now i know how to handle it.