09-23-2019 02:53 PM
Hi All,
I have the following equipment:
1. proportional valve - https://www.aliexpress.com/item/33040257963.html
2. Frequency converter - https://www.amazon.com/KNACRO-Frequency-Voltage-Conversion-Converter/dp/B06XZFKPHP/ref=sr_1_fkmr0_2?...
3. NI9201 for reading voltage inputs
4. NI9263 for sending voltage outputs (to the porportional valve).
This valve is capable of sending PWM outputs, and I am trying to convert that to DC voltage so it can be read by NI9201 (please see attached picture). I expect that when I move the ball valve, the output frequency from the valve will change, which then be converted to DC voltage. After the connection has made, labview is picking up a voltage signal 4-5V. However, when I change the position of the ball valve. labview is still reading the same 4 to 5V signal.
Does anyone have any idea what would be the issue?
Note. I have not calibrated the converter, but this should not be the reason why it is not picking up the changes in signal.
Thanks!
Solved! Go to Solution.
09-25-2019 08:09 AM - edited 09-25-2019 08:17 AM
That's why you have to use a PWM to voltage converter.
09-25-2019 01:27 PM
I was beginning to have doubt about this PCB as well as the manual did not really mention anything about PWM.
Much appreciated for the response!