hi flo!!!
help please!!!
how I can change P2012 and P2013 in mm440 or you uss library??? becouse I have error 5008(incorrect byte count) if baud rate 9600 or error 5007(missing STX) if baud rate 38400
08-04-2010 05:11 PM
Is there a way to have these libraries in 8.5 LabView version please?
I am developing a project with some 420 and 440 drives, and it would be great to use this library.
Best regards,
Gilberto Garza
08-05-2010 06:11 AM
Dear Gilberto,
I have conerted the files Flo has posted to LabVIEW 8.5 format, I hope it will work for you. If it doesn't or if you have any other questions, please don't hesitate to ask.
Have a wonderful day!
08-05-2010 08:40 AM
Thank you very much Zenon, it will help me a lot!
Best regards,
Gilberto Garza
10-06-2010 10:04 AM
Do you have the files available for LabVIEW 8.2?
10-07-2010 01:27 AM
Dear Parga,
I converted the files for LabVIEW 8.2, nevertheless there were some changes in several of the used VIs, so I'm not sure if it will work for you. Can you please check and let me know if it did work or not?
Thanks you!
10-07-2010 03:09 AM
Dear Zenon,
Let me play with the files and my inverter for a couple of days and then I will let you know if I have troubles with them.
Thank you very much for your promptly support.
Regards,
Abraham Parga
03-28-2011 07:16 PM
Thank you very much, I am working with the MM420 now and the PZD is max of 4 words, do I have to modify the vi PZD_USS.vi to make it work?
Best regards,
Gilberto Garza
03-29-2011 02:01 AM
The original library expects PZD=8. So you will have to dive into the code to alter it. Not sure about the altered llb intended for MM440 but if it now reads also 8 words, it will be same case.