Dear Mr.Jochen,

 

This is a new post regarding Contour moves.

 

As the velocity of a contoured move is determined by the distance between the position points in the contour array. Request you to kindly help us out in sorting out few problems.

  

Our application is Dual axes linear motion of 1 meter length. Each axis consists of  an AC Drive, Linear motor and linear incremental encoder of resolution 25 microns (1 mm = 25 counts). The maximum speed of the system is 2 m/s.

  

We could achieve the maximum speed in Absolute position mode. And could successfully make a contour move of different patterns upto 0.5 m/s in Absolute contouring. But unable to achieve beyond 0.5 m/s.

 

1. Kindly give us sample points in counts where we can achieve 2 m/s. 

 

2. The contour move always starts from zero, Can we make contour moves which start from a Non-zero point. Also the contour move should be continuous.

 

Thanking you,

 

Waiting for your reply.

 

Regards.

  

 

 

 

0 Kudos
Message 1 of 12
(4,358 Views)

Hello Vanisp,

 

it's very kind from you, that you address me directly, but as this is a public forum there is a whole community monitoring it. Smiley Very Happy

 

Anyway. Could you please  explain a bit more in detail what happens if you exceed the velocity limit of 0.5 m/s? Do you get an error? Could you please post a log file that contains your contouring data?

 

Contouring operations are always relative to the start position. So e. g. if you move your axis to position 10000 and start a contouring operation, that starts with "0, 1, 4, 8,..." in the position buffer, this doesn't mean, that the axis jumps back to these absolute positions. Instead the absolute positions of this move start with "10000,10001, 10004, 10008,..." (this example is valid for Absolute Contouring Mode. Please refer to the documentation of "Set Operation Mode" for more details).

 

For continuous contouring operations please refer to the example "Buffered Contouring(Rose).vi". In fact the maximum number of contouring points for a single contouring operation is 2^32 values. With a update period of 20 ms this equals to 497 days of continuous operation, which should be enough for the vast majority of applications.

 

Kind regards,

Jochen Klier

National Instruments

 

Message Edited by Jochen on 01-27-2010 01:39 PM
0 Kudos
Message 2 of 12
(4,353 Views)

Dear Sir,

 

We get an error message stating "overcurrent" from the drive when I increase the velocity (higher than 0.7 m/s). Kindly have a look at the contour array. The contour array generates figure 8 pattern. Please let me know if any further details are required.

 

29.40000 0.660 1041.900 91.140 1854.090 293.670 2630.220 607.230 3355.170 1025.760 4014.780 1541.130 4596.270 2143.260 5088.300 2820.480 5481.270 3559.590 5767.560 4346.190 5941.620 5164.950 6000.000 6000.000 5985.390 6418.530 5868.900 7247.460 5638.170 8052.120 5297.700 8816.820 4854.090 9526.710 4316.040 10167.960 3693.960 10728.060 3000.000 11196.150 2247.630 11563.110 1451.520 11821.770 627.1800 11967.120 -209.400 11996.340 -1041.900 11908.860 -1854.090 11706.330 -2630.220 11392.770 -3355.170 10974.240 -4014.780 10458.870 -4596.270 9856.740 -5088.300 9179.520 -5481.270 8440.410 -5767.560 7653.810 -5941.620 6835.050 -6000.000 6000.000 -5941.620 5164.950 -5767.560 4346.190 -5481.270 3559.590 -5088.300 2820.480 -4596.270 2143.260 -4014.780 1541.130 -3355.170 1025.760 -2630.220 607.230 -1854.090 293.670 -1041.900 91.140 209.4000 -3.660 1041.900 -91.140 1854.090 -293.670 2630.220 -607.230 3355.170 -1025.760 4014.780 -1541.130 4596.270 -2143.260 5088.300 -2820.480 5481.270 -3559.590 5767.560 -4346.190 5941.620 -5164.950 6000.000 -6000.000 5941.620 -6835.050 5767.560 -7653.810 5481.270 -8440.410 5088.300 -9179.520 4596.270 -9856.740 4014.780 -10458.870 3355.170 -10974.240 2630.220 -11392.770 1854.090 -11706.330 1041.900 -11908.860 209.4000 -11996.340 -627.180 -11967.120 -1451.520 -11821.770 -2247.630 -11563.110 -3000.000 -11196.150 -3693.960 -10728.060 -4316.040 -10167.960 -4854.090 -9526.710 -5297.700 -8816.820 -5638.170 -8052.120 -5868.900 -7247.460 -5985.390 -6418.530 -5985.390 -5581.470 -5868.900 -4752.540 -5638.170 -3947.880 -5297.700 -3183.180 -4854.090 -2473.290 -4316.040 -1832.040 -3693.960 -1271.940 -3000.000 -803.850 -2247.630 -436.890 -1451.520 -178.230 -627.180 -32.880 0.000000 0.000 0.000000 0.000

 

 

 Kindly help us out.

 

Regards,

Vani

 

 

0 Kudos
Message 3 of 12
(4,308 Views)

Vani,

 

if your drive runs into an overcurrent situation, this typically means, that the acceleration values are too high (current is proportional to torque and torque is proportional to acceleration).

Looking at your  contouring data, this might be the case (e. g. there is a jump from 29.4 to 1041.9 in the beginning). I don't know, what this jump means in terms of physical acceleration, but you should be able to calculate that.

 

Please double check the accelerations generated by your contouring profile and adjust them accordingly.

 

Kind regards,

Jochen

0 Kudos
Message 4 of 12
(4,286 Views)

Dear Sir,

 

Please have a look at this contour array given in the attachment. This array was generated from MOTION ASSISTANT for the move constraints given below.

 

Velocity = 0.75 m/s (which is 30000 counts/s)

Acceleration = 3.75 m/s2 (150000 counts/s2)

Deceleration = 3.75 m/s2 (150000 counts/s2)

 

Here too we get the same error message. 

 

x-axis : 29, 39, 69, 119, 188 ,................

y-axis : 0, 1, 4, 8, 13, 19, .................

 

Waiting for your reply. 

 

Thanking you,

 

With regards,

Vani

0 Kudos
Message 5 of 12
(4,280 Views)

Vani,

 

overcurrent means too much torque. It's that simple. If you don't run into this problem with an Absolute Move, there might be differences between this operation mode and the contouring mode in terms of forces that occur in your mechanical system.

 

Maybe you need to optimize the tuning of your PID parameters. I could imagine, that the contouring profile introduces oscillations to your axes and you need to tune the control loops for better damping.

 

If tuning is the potential source of this issue, please refer to this document.

 

Kind regards,

Jochen

 

0 Kudos
Message 6 of 12
(4,275 Views)

Dear Sir,

 

Please find an attachment of the step response of the system and kindly suggest.

 

 

Thanking you,

 

Regards,

S.P.Vani 

 

0 Kudos
Message 7 of 12
(4,219 Views)

The step response doesn't look too bad, but you could try to get a critically damped system (without overshot) by increasing Kd. If the system becomes a bit nervous, you could increase Td to 3 - 5.

As your system doesn't settle to the exact target position, I guess your Ki value is zero. Setting Ki to a low value (e. g. 1 or 2) and decreasing the integration limit to a quite low value (e. g. 100 to 200) could result in better static accuracy, but it also tends to add an overshot, so you should be careful with that.

 

 

0 Kudos
Message 8 of 12
(4,216 Views)

Dear Sir,

 

As the mechanical system is not available with us, we are unable to fine-tune and check the step response. 

 

Can you please advice us what could be our next step which can be done. 

 

Thanking you,

 

Regards,

Vani 

0 Kudos
Message 9 of 12
(4,089 Views)

Dear Sir,

 

I would also like to mention few details regarding the mechanical system. The total force required to run the system is 90 N (F=ma = 18 Kg * 5m/s2). 5m/s2 corresponds to 2,00,000 counts/s2 in MAX. This excludes external frictional forces and static friction. 

 

Motor Specification: -

 

Motor peak force = 213N

Max. force at speed 2 m/s = 134N (63% of 213). 

Here Duty cycle = 100% 

Max. force at 100% duty cycle = 40% of total available force (40% of 134) = 54N.

 

The max. available force = 54N and the required force = 90N. We are able to achieve upto 1m/s speed for this load. Is the acceleration too high for this application? Or do I have to procure a motor that has got a capacity to produce more force? 

 

Also with NO LOAD condition and acceleration 8 m/s2, we were able to achieve 1.7 m/s speed in absolute contouring mode. 

 

We will surely try to get a critically damped system after we get the mechanical system. Kindly advice what could be possibly done. 

 

Thanking you,

 

Regards,

Vani 

 