Hello!

 

I am using the PXI 8431/2 to read out data from the PDS ELITE flowmeter (Modbus RTU). For receiving data, the RS485 protocol asks for pin 4 and 5, but this configuration does not seem to work. When I connect the RS-485 to USB converter from Microflex I do receive the data properly, so somehow between the pin lay out and the PXI there is this problem.

 

Can somebody help me out?

 

Cheers,

 

Steven

0 Kudos
Message 1 of 5
(7,560 Views)

Hello,

 

Could you check the below link?

 

http://force.natinst.com:8000/pls/ebs/niae_screenpop.main?p_incident_number=877874

 

Hope this helps.

 

Kind regards,

Hossein

0 Kudos
Message 2 of 5
(7,556 Views)

Hello Hossein,

 

your link is not working. Even https://force.natinst.com/ is not found with my browser...

 

Rgds,

 

Steven

 

 

0 Kudos
Message 3 of 5
(7,553 Views)
Solution
Accepted by topic author StevenSablerolle

Hello Steven,

 

I think what Hossein was trying to send you is this:

 

How do I Connect and Configure a 2-Wire Device With RS-485

 

Can you also tell me a bit more what you are using to read the data? What environment. Do you have 2 wire or 4 wire Modbus RTU?

 

Regards,

 

Rik Prins, CLA, CLED
Software Development Engineer
0 Kudos
Message 4 of 5
(7,543 Views)

Hello Rik,

 

thank you very much! As I followed the link, we have shortcutted pin 4 with 8 and 5 with 9. Setting the it to half-duplex, the transmitter and receiver data can now go through the 2 wire cable.

 

Best regars,

 

Steven