04-09-2007 06:59 AM
04-09-2007 10:06 AM
Most likely the process file is for whatever reason corrupted. You can recompile the source by opening the .lks file. Good luck!
07-28-2016 11:44 AM
I started having the same problems, when I try to recompile by opening the source file I get 'Compile Failed'. The error is 'Object is not defined: Invalid signal'.
07-28-2016 11:56 AM
Can you provide more detail of the compile error?
07-29-2016 10:48 AM
07-29-2016 11:47 AM
Open the source file (ebbpsrv.lks) in a text editor and search for INVALIDSIGNAL. There will probable be two, one on or near line # 1120 and another on or near line # 23125. You can delete the INVALIDSIGNAL text and try to recompile, but you may have to delete the object definition completely. You can create a new process file with only the object causing the problem to copy a 'clean' object definition into your ebbpsrv.lks file and then hopefully (fingers crossed) it will compile.
08-01-2016 08:27 AM
That worked, thank you very much !!!
08-01-2016 11:40 AM
It happened again, so I copied fresh working files (l4p,l4t,lka,lks) from a backup machine. The process file will run each time without any problems until I do a compile from the source file, it fails with 'compile failed', but now when I run the process file I'm back to the ''Not a Lookout process file' error. It looks like the Lookout executable is corrupting the files. There was something similar a few years back with a ABS function bug that required a patch.
08-05-2016 06:18 AM
The problem was caused by previously configured points not being completely removed and the process file was saved, creating a bad source file that was never compiled, then all was saved to backup.
03-14-2017 11:57 AM
Thanks for this awesome detailed solution.