"Bob laragione" wrote:
>>I am using Looout 4.01and FieldPoint equipment.My process runs fine in
the>development mode.>I then load the files to Lookout client and a message
saying "cannot find>FieldPoint cbx file" appears.>Yet all the files are in
the directory!!>>Not Happy!!!>>Thanks for the time...
Bob,
Client versions of Lookout are not capable of using driver objects. A client
should have all of it's connections linked back to a server using absolute
paths. The primary objects for clients tend to be things like pot, switches,
pushbuttons, hypertrends and symbolic links. If you want a program that is
a stand-alone process that is interfacing with FieldPoint, you will need
a run-time system. Client systems can solely link to Development/Runtime
serve
rs.
Aaron