In Lookout 6.2 how can I send an email when an alarm has deactivated or cleared?

I need to send an email when an alarm has deativated. Such as, AC power fails and the generator is running. Whne the AC power is restored, I want to send an email as well as when the generator stops running. I have created mailer objects to do this based on the data member for each being "false". The problem is, that if the system does a restart then emails go out for all of those data members because they start up as "false" in the normal condition. Anyone have a suggestion?

 

Thanks

 

Brad Adams

Communications Group Inc.

brad@commtechradio.com

0 Kudos
Message 1 of 2
(5,502 Views)

Simplest way i can think of is a FlipFlop or a latchgate obect to ensure it did start first.  Reset the flipflop/latchgate when the email is sent.

 

Mike

Mike Crabtree - Lead Developer
Destek of Nevada, Inc. / Digital Telemetry Systems, Inc.
(866) 964-6948 / (760) 247-9512
0 Kudos
Message 2 of 2