How to configure multiple counters to operate as one large counter with cFP-CTR-502 ?
0 Kudos
Message 1 of 2
(2,236 Views)
  1. Wire your signal into the input of counter 0.
  2. Set counter 0 attributes to the following:
    Count Source: External Count Input
    Terminal Count: 65535
    Gate Source: Always Enabled
    Read Reset Mode: Don't Reset on Read
    Noise Rejection: 50 kHz
  3. Set counter 1 attributes to the following:
    Count Source: Previous Channel
    Terminal Count: 65535
    Gate Source: Always Enabled
    Read Reset Mode: Don't Reset on Read
    Noise Rejection: 50 kHz
  4. Create a Control @Multi channel by checking both channel 0 and channel 1 and then clicking on Create Item in the Channel Commands section.
  5. Save the iak file.