I'm curious why you decided to build a CIN instead of developing the code in
LabVIEW. Is there some functionality that that LabVIEW couldn't
provide? Can you provide some more information about the LabVIEW
Real-Time target you're using? What type of IO are you using?
It is impossible to get LabVIEW Real-Time performance on a desktop PC running
an OS other than LabVIEW Real-Time. Even running a timed loop in LabVIEW
for Windows won't guarantee a jitter free application. Also, no TCP based
network communication can be deterministic. This means Network Shared
Variables are also not deterministic (they use a TCP for data transport) and I
advise against using them as a means to send time critical control data between
a Windows host and a LabVIEW Real-Time application.
In general, I would architect most LabVIEW-based control applications as
follows:
- Write all control logic and IO operations in LabVIEW Real-Time. The
LabVIEW Real-Time application would accept set points and/or commands from the
'host' (desktop PC). The Real-Time controller should be capable of
running independently or automatically shutting down safely if communication to
the PC is lost.
- Write a front-end user interface in LabVIEW that runs on the desktop
PC. Use Shared Variables with the RT-FIFO option enabled to send new set
points and/or commands to the LabVIEW Real-Time target.
Shared variable buffering and RT-FIFOs can be a little confusing. Granted
not all control applications are the same, but I generally recommend against
using buffering in control applications and in LabVIEW Real-Time applications
recommend using the RT-FIFO option. Here's why: Imagine you have a
Real-Time application with two timed loops. Time-loop 'A' calculates the
time critical control parameters that get written to hardware output in
timed-loop 'B'. Loop 'A' writes the outputs to a RT-FIFO enabled variable
with a RT-FIFO length of 50. Loop 'B' reads the outputs from the shared
variable, but for some reason, if loop 'B' gets behind then the shared variable
RT-FIFO will now contain several extra elements. Unless loop 'b' runs
extra fast to empty the RT-FIFO, loop 'B' will now start outputting values that
it should have output on previous cycles. The actual desired behavior is
that loop 'B' should output the most recent control settings, which means you
should turn off buffering and set the RT-FIFO length to 1.
There is also a clear distinction between buffering and the RT-FIFO
option. The RT-FIFO option is used to add a non-blocking layer between
network communication and time-critical code in LabVIEW Real-Time
applications. It also provides a safe mechanism to share data between two
loops running in a Real-Time application without introducing unnecessary
jitter. Network buffering is a feature that allows a client to receive
data change updates from the server even if the client is reading the variable
slower than the server is writing to it. In the example I presented above
you don't need to enable networking because the shared variable is used
entirely within the Real-Time application. However, it would be
appropriate to send control set points from a Windows PC to the Real-Time
application using network published shared variables with the RT-FIFO option
enabled. If it is critical that the Real-Time application executed all
commands in the sequence they were sent then you could enable an appropriate
buffer. If the control application only needs the latest set point
setting from the Windows host then you can safely disable network buffering
(but you should still enable the RT-FIFO option with a length of 1 element.)
Network buffering is especially good if the writer is 'bursty' and the reading
rate is relatively constant. In the robot application I can imagine buffering
would be useful if you wanted to send a sequence of timed movements to the
Real-Time controller using a cluster of timestamp and set point. In this
case, you may write the sequence values to the variable very quickly, but the
Real-Time controller would read the set points out as it proceeded through the movements.
The following document presents a good overview of shared variable
options: http://zone.ni.com/devzone/cda/tut/p/id/4679