10-29-2019 11:07 AM
I need to communicate with a MODBUS slave through RS232, and the documentation for the slave specifies that there should be no stop bit. As far as I can tell, Labivew doesn't let you configure a serial port with no stop bit. Is there some way to do this?
Solved! Go to Solution.
10-29-2019 11:19 AM - edited 10-29-2019 11:22 AM
It might be worthwhile taking a look at one of the MODBUS libraries available for LabVIEW. They probably have built-in handling for several MODBUS-specific issues.
One library is built in if you have either the "DSC Module or Real-Time Module", according to the help files.
Others include LabVIEW-Modbus-API or the older MODBUS Library for LabVIEW.
The first of those links provides an overview of some of the others, copied below (original author is smithd):
Modbus is a commonly used protocol for industrial communication. At present, National Instruments provides four options for Modbus connectivity.
(1) Modbus I/O server, available through the LabVIEW Real-Time Module or the LabVIEW Datalogging and Supervisory Control (DSC) Module.which provides a high-level API for accessing Modbus data. Learn more at Connect LabVIEW to Any PLC With Modbus
(2) A free Modbus library available for download which is very low-level, and provides control over Modbus not offered by I/O servers at the expense of the connection management and request scripting offered by that higher-level API. **This Library is Unsupported**
(3) This NI Labs Modbus API release which is intended as a replacement and expansion of the free Modbus library functionality. **This Library is Unsupported**
(4) The Modbus API available through the LabVIEW Real-Time Module or the LabVIEW Datalogging and Supervisory Control (DSC) Module. This is a version of the NI Labs Modbus API which is now supported and maintained by National Instruments R&D.
In addition, an NI Alliance Partner SAPHIR has two released LabVIEW add-on products called ModBusVIEW over TCP and ModBusVIEW over Serial available on the LabVIEW Tools Network.
10-29-2019 11:20 AM
10-29-2019 11:24 AM
Thank you for your reply. It's a Lytron recirculating chiller, manual attached. The relevant information is on page 28.
10-29-2019 11:25 AM - edited 10-29-2019 11:33 AM
@GerdW wrote:
Hi Tristan,
mind to name that slave and attach (or link to) the manual?
Oh, no Problem! I'll just shake the reliable 8-Ball and
~~~~Outlook uncertain~~~~
OK, I cross posted with the OP ( How did I miss That! Silly 8-Ball needs to be re calibrated)
8,none,&1 is the default for RS-232 but you seem to be describing a MODBUS-RTU via ethernet? What is the PHY layer?
10-29-2019 11:37 AM
Thanks for the reply. I'm using RS232, not ethernet. My problem is with the number of stop bits, which can only be 1, 1.5, or 2, as far as I can tell. Am I missing something?
10-29-2019 11:51 AM
What you are missing is that the manual is wrong and needs editing. You can't have a serial communication without a stop bit.
8-n-1 means 8 data bits, No parity, 1 stop bit.
10-29-2019 11:55 AM
Could the manual have a typo?
19.2,N,8,1
would normally mean Baud=19.2, No Parity, 8 Data, 1 stop
I have never come across No stop bit!
10-29-2019 12:01 PM
Thank you! That worked.
10-29-2019 01:42 PM
Hint: you can have mark more than one replay as a solution. I can see at least one other post that deserves a solution - and it came before the one you marked.