02-05-2018 07:50 AM
I have a problem connecting to an OPC UA server. I used the simplest version of NIs Example here
but no matter what I do i get the error
-356653 The status of the OPC UA server is uncertain.
I have tried setting the "trust all servers" to true, i have tried providing certificates... nothing works. Other software such as UA expert connects instantaneously without any issues. How hard can it be?
06-20-2018 04:39 AM
We have the same problem here connecting to a B&R plc.
We tried different settings for authorization in combination with provided certificates, but this does not work at all.
Connection with UA expert works fine.
@bfelber: have you solved the problem in the meantime?
06-20-2018 06:20 AM
Yes, we solved it by using the hostname "br-automation" - or whatever hostname is configured in automation studio - instead of the ip address. Just add the plc's ip to your host file in the system32/drivers/etc folder. With this workaround you should be able to connect to your B&R plc. I hope this will work out for you as well.
06-20-2018 07:12 AM
Works perfectly, thank you very much!
For everybody else encountering this problem, see screenshot attached for solution.
06-27-2019 03:01 AM
Thank you very much guys! I had the same issue with B&R and now it has been solved 🙂
06-27-2019 06:18 AM
@diebestetest wrote:
Thank you very much guys! I had the same issue with B&R and now it has been solved 🙂
we solved it by using the hostname "br-automation" - or whatever hostname is configured in automation studio - instead of the ip address. Just add the plc's ip to your host file in the system32/drivers/etc folder. With this workaround you should be able to connect to your B&R plc.