OPC UA connection problem

I have a problem connecting to an OPC UA server. I used the simplest version of NIs Example here

 

https://zone.ni.com/reference/en-XX/help/371618J-01/lvmve/establishing_connection_btwn_opcua_svr_cln...

 

but no matter what I do i get the error

 

-356653 The status of the OPC UA server is uncertain. 

I have tried setting the "trust all servers" to true, i have tried providing certificates... nothing works. Other software such as UA expert connects instantaneously without any issues. How hard can it be?

 

Message 1 of 6
(4,733 Views)

We have the same problem here connecting to a B&R plc.

 

We tried different settings for authorization in combination with provided certificates, but this does not work at all.

Connection with UA expert works fine.

 

@bfelber: have you solved the problem in the meantime?

0 Kudos
Message 2 of 6
(4,534 Views)

Yes, we solved it by using the hostname "br-automation" - or whatever hostname is configured in automation studio - instead of the ip address. Just add the plc's ip to your host file in the system32/drivers/etc folder. With this workaround you should be able to connect to your B&R plc. I hope this will work out for you as well.

Message 3 of 6
(4,519 Views)

Works perfectly, thank you very much!

For everybody else encountering this problem, see screenshot attached for solution.

 

opc_ua.PNG

 

0 Kudos
Message 4 of 6
(4,511 Views)

Thank you very much guys! I had the same issue with B&R and now it has been solved 🙂

0 Kudos
Message 5 of 6
(3,795 Views)

@diebestetest wrote:

Thank you very much guys! I had the same issue with B&R and now it has been solved 🙂


we solved it by using the hostname "br-automation" - or whatever hostname is configured in automation studio - instead of the ip address. Just add the plc's ip to your host file in the system32/drivers/etc folder. With this workaround you should be able to connect to your B&R plc.