07-26-2013 02:01 PM
Looks like the NI 9220 is not supported by cRIO scan mode:
http://www.ni.com/white-paper/8136/en/
It's mostly a sign of inadequate communication between the hardware and software sides of my project, but this threw a major wrench in my gears recently. I wasn't anticipating any difficulties like this because it doesn't seem like a super exotic module. Anyone know if there are plans in work to have this module supported?
11-21-2016 04:07 PM
Since I've seen this post referenced a few times, I would like to call out that the 9220 IS supported by Scan Mode. Please see the link in the original post as this is a living document and updated regularly.
11-21-2016 05:02 PM
Jon,
I recently ran into this issue. To use the 9220 with cRIO Scan Mode Interface requires (minimum):
LabVIEW 2015, CompactRIO drivers August 2015, and LabView 2015 Real-Time module.
Reference:
ftp://ftp.ni.com/pub/gdc/tut/crio_software_versions.htm
On this page, Select: C Series modules and accessories, then NI 9220.
steve