Hi All,
Setup: Read Modbus Registers (Serial) of modbus slave.
When the initialization of the code is taking place, i get the warning
Status Code 1073676294 (Hex 0x3FFF0006)
maps to a status report. The status code indicates The Number of Bytes Transferred is Equal to the Input Count. More data might be available.
I have read some threads, but they are getting this error when reading, but i am getting this error in modbus master's (Mod Init) subvi where the port initializzation is taking place before reading & writing.
In extentation, if the slave device gives timeout then the modbus master does not poll the slave, can the above warning is responsible for this issue.
Regards,
Shrenik
08-09-2011 01:15 AM - edited 08-09-2011 01:15 AM
Hi Shrekt,
The warning is not creating any issue for you read and write function.
If you are getting timeout error then probably you have to check your device configuration means your device ID or Mode.
Verify your register address with your device manual, if some mismatch is there this will give you timeout error.
Sometime some device manuals represents that the to read the value register address is 1,2,3,......
But in actual program you have to read it with 40001,40002 like that. So try this also.
Thanks and Regards
Himanshu Goyal
08-09-2011 01:27 AM
Thank you for the reply,
My communication the slave device is OK, but sometime if timeout is there for half an hour then it fails to reconnect.
Regards,
Shrek
08-09-2011 01:41 AM - edited 08-09-2011 01:42 AM
Hi,
If your communication is OK and sometime you got timeout then you have to check your time delay.
The Time synchronization plays a major role in your serial communication. Try with some different time delay.
Thanks and Regards
Himanshu Goyal