Tried Snapshot.
Same situation.
The configuration under MAX is correct.
The configuration under LV Project is not.
02-25-2007 09:45 PM
Hi Wes_OH,
If you would like to transfer the settings from MAX to your LabVIEW project,
first, make sure you have FieldPoint 5.0.1. You can verify this by
looking in the Software tab in MAX. If you do not have that version of
the driver, you can download it here.
After you have verified that you have the correct version of the FieldPoint
driver, you will be able to import the .iak file from MAX to your LabVIEW
project. Open your LabVIEW project, right-click on the Project Title in
the Project Explorer »Import» FieldPoint Configuration. Then, find you
.iak file in the File Dialog box that appears. This will import the
custom scale that you configured in MAX.
If you just add a new target to your project, the .iak configuration is not
imported.
Please let me know if you have any further questions. Best of luck on
your application, and have a great day!!
02-26-2007 07:12 AM
Thanks.
I was able to import.
However, I still have the problem.
The scaling appears to have no effect on the output.
I'm using the example Analog Output VI that comes with LV.
Using the correct IAK with the scaling slope 1.6 and y-intercept 8 on channel 2 of cFP AO module.
When I adjust the dial on the VI to change the voltage, it ranges from 0-10V and the actual voltage seen at the terminals of the AO are identical with no scaling.
What I want to see is 8-12PSI on the dial and 0-10V on the terminals.
The scaling should convert between the two.
What I'm seeing is 1:1 . Dial setting digital display is identical to the actual terminal output.
No scaling is occuring.
02-26-2007 10:02 AM
I've found that if I create a new VI under project, that it functions properly and the ranges of my control are scaled yielding the expected output on the terminals of the AO module.
However, if I use the existing AO VI this is not the case.
I believe it has something to do with this example VI using an array of controls and their being inter related not having the ability to excercise independent range values and scaling.
Is this correct?
02-27-2007 10:43 PM
02-28-2007 06:00 AM
Yes.
Only works with single control passing data to single channel.
Tried cluster as well, but the FP Write VI requires a 1-D array for multiple inputs so had to use Cluster to Array which put me back in the same situation.
03-01-2007 04:36 PM
03-02-2007 06:06 AM
I need to scale each channel independently.
Each channel of the AO represents a simulation signal for a particular measurement type (ie. channel 0 = temp, channel 1 = windspeed)
In the real-life system, these volt values come from various devices such as thermocouple, and aneometer.
For each measurement, the voltage values would represent a unique measurement type and have unique ranges and scaling.
Where 2 volts may represent 50C in temperature on channel 1 and 3 volts may represent 10MPH on channel 1.
We are simulating real-life conditions in a lab environment.
03-05-2007 11:13 AM - edited 03-05-2007 11:13 AM
Hey Wes
So I'm kinda jumping in during the middle of your conversation here, but as I read back through the forum I have a number of questions. I know that you have configured your FP items in max with the scaling you want. I assume that you changed the individual channels on your AO, not the "all". You save your IAK file, and it successfully downloads to your controller. You then open LabVIEW, create a new project and import the IAK file. My first question is:
Do you see the custom scale you created if you right click on the channel of interest in the project, go to properties and then look at the custom scaling tab? (Again, I assume you're not using the "all" channel).
If not, I was able to have some luck scaling directly from the project instead of using MAX. So my second question is:
Are you able \ willing to create the scales as part of the project instead of through MAX?
Post back and let us know what you find. Thanks!
Chris C
Message Edited by Chris_C. on 03-05-2007 11:13 AM